It's been a long day and my brain has long since departed. Here's the latest issue I'm working on:
I've got a building with a 400A 120/208Y service
They have a water pump that was recently replaced, now popping the breaker.
Pump is 15HP 3PH 575V 19A nameplate, running about 17A
It's connected via a 30KVA 208Y/600Y autotransformer, with X0 left floating
Now I calculate that with the pump running around 17A the autotransformer should be drawing about 48A, yet it's tripping a 60A breaker after about 10 minutes.
The only thing I can thing of is that perhaps there is a voltage imbalance on the source side. If the legs are unevenly loaded ahead of the autotransformer, could that create enough voltage imbalance and/or current imbalance to pop the breaker? Is it worth the effort to replace the 3C6 cable feeding the autotransformer with 4C6?
I've got a building with a 400A 120/208Y service
They have a water pump that was recently replaced, now popping the breaker.
Pump is 15HP 3PH 575V 19A nameplate, running about 17A
It's connected via a 30KVA 208Y/600Y autotransformer, with X0 left floating
Now I calculate that with the pump running around 17A the autotransformer should be drawing about 48A, yet it's tripping a 60A breaker after about 10 minutes.
The only thing I can thing of is that perhaps there is a voltage imbalance on the source side. If the legs are unevenly loaded ahead of the autotransformer, could that create enough voltage imbalance and/or current imbalance to pop the breaker? Is it worth the effort to replace the 3C6 cable feeding the autotransformer with 4C6?