autotransformers & EC motors

kjunlandr

Member
Location
Jasper, GA
Occupation
Commercial Refrigeration Manufacturer Technical Support
What would cause the failure of a 230V rated EC condenser fan motor on the common side of a 600v x 230v autotransformer on a new start up? I do know if the there is a break in the common side of said AUTRNSFMR 600V would then be applied to the 230V load.
 

winnie

Senior Member
Location
Springfield, MA, USA
Occupation
Electric motor research
A 600V:240V autotransformer would have vastly different L-G voltage than a typical 240V source. Filter and TVS components are often connected L-G, and DC bus insulation is based on the L-G voltage.

Jonathan
 