bill talbot
Member
A customer wants us to use a 45kVA 480/575V 3 phase auto transformer for a test/research project. On the 575V side we are required to install two fusible safety switches, one a 30A 3P for control, the other switch will be a 60A 3P for load protection, which I would classify as two taps. The 480V side will be protected by a single 70A 3P CB.
The building distribution system is 480/277V 3 PH 4W.
Under testing functions the current will initially flow from the 480V side through the transformer to the 575V load side. After a short time the current will the automatically reverse, flowing from the 575V side to the 480V side supplying a minimal amount of reverse power which will be absorbed by the building power needs but not enough to export into the utility.
We advised our client that Art 450.4(A) prohibits an overcurrent device in series with the shunt winding which, in our case, is the 480V side where we have the 70A CB. Our client who is an EE, is urging us to complying with his requirements, confident that the AHJ will have no problem with this arrangement. I addition, we are not comfortable with power flowing backwards through the fusible switches either but these could be changed to CB's.
What are your thoughts?
The building distribution system is 480/277V 3 PH 4W.
Under testing functions the current will initially flow from the 480V side through the transformer to the 575V load side. After a short time the current will the automatically reverse, flowing from the 575V side to the 480V side supplying a minimal amount of reverse power which will be absorbed by the building power needs but not enough to export into the utility.
We advised our client that Art 450.4(A) prohibits an overcurrent device in series with the shunt winding which, in our case, is the 480V side where we have the 70A CB. Our client who is an EE, is urging us to complying with his requirements, confident that the AHJ will have no problem with this arrangement. I addition, we are not comfortable with power flowing backwards through the fusible switches either but these could be changed to CB's.
What are your thoughts?