The NEC has the requirement that if a ground electrode is present at the time of construction, then it MUST be used. This can be seen in 250.50 below.
250.50 Grounding Electrode System.
All grounding electrodes as described in 250.52(A)(1) through (A)(7) that are present at each building or structure served shall be bonded together to form the grounding electrode system. If none of these grounding electrodes exist, one or more of the grounding electrodes specified in 250.52(A)(4) through (A)(8) shall be installed and used.
However, 250.54 says that if you add Auxiliary Grounding Electrodes, they do not need to comply with 250.50. See below:
250.54 Auxiliary Grounding Electrodes.
One or more grounding electrodes shall be permitted to be connected to the equipment grounding conductors specified in 250.118 and shall not be required to comply with the electrode bonding requirements of 250.50 or 250.53(C) or the resistance requirements of 250.53(A)(2) Exception, but the earth shall not be used as an effective ground-fault current path as specified in 250.4(A)(5) and (B)(4).
Here is a thought experiment I have been running through my head:
If I have my ground electrode system and I do all my bonding near my service (GEC, MBJ, electrode bonding jumpers, the works), but I also have some remote equipment, say on opposite side of a river, for whatever reason my heart desires, I want to drive a few ground rods there at the time of construction. I assume these to be auxiliary ground electrodes. I plan to install a large terminal cabinet on the opposite side of the river and have a ground bus bar that is 1⁄4 in. thick × 2 in wide x length as required. I plan to land my ground electrode bonding jumpers from the auxiliary electrodes to the ground bus bar in the terminal cabinet. I also plan to land my EGC from my feeder that traverses from one side of the river to the remote equipment terminal cabinet.
At what point do those auxiliary electrodes stop being auxiliary electrodes? Section 250.64(F) allows you to interconnect your ground electrode system electrodes via a ground bus bar. I assume since my interconnection across the river is through an EGC, that is what determines the auxiliary status of those remote electrodes? What if the EGC was of sufficient size to be a ground electrode bonding jumper, say due to upsizing as a result of voltage drop? Do those auxiliary ground rods stop being auxiliary? Does the fact that they were available at the time of construction mean that I need to treat them to meet 250.50?
Taking this thought experiment 1 step further:
Suppose you are wiring a detached garage. You install a 30A "subpanel" in the garage. You send a feeder of #10/3. You land your EGC in the panel from the feeder, you run a Ground electrode bonding jumper from 2 ground rods that you drove near the detached garage to the ground bar in the panel. Can it be thought of that the ground electrodes at the garage are auxiliary ground electrodes in the eyes of the main service ground electrode system (complying with 250.54 in reference to the main service GES) and the actual ground electrodes of the ground electrode system of the garage (complying with 250.50 in reference to the garage)?
If you read down this far, thank you.