First of all there's only one circumstance I would install an auxiliary grounding electrode for a rooftop array: if the AHJ forced me to. Mike Holt has done a half-hour video one why it is a useless and possibly dangerous idea. You didn't say what code you're trying to follow but auxiliary electrodes have been removed from the 2017 and 2020 NEC. I think they are a fundamental misunderstanding of what grounding is and does.
(For a ground mount, there might be some lighting protection utility to a ground ring that surrounds the whole installation; I'm not enough of an expert to say. I do think I'm enough of an expert to say that a ground rod for a ground mount won't do a thing, especially if the ground mount is supported by numerous metal piers that effectively meet the requirements for building steel to be an electrode.)
(Another thing that might muddy the water is if the array is on a detached building that has no other power. If that's your situation let us know.)
So as far as your question...
It's kind of unclear what you're asking, but the answer is pretty clearly no.
For an auxiliary array electrode, you install a Grounding Electrode Conductor between the equipment (solar array) and the electrode in the ground. That's it.
Note that you still need an EGC from the array back to your ground bar at your inverter or micro-inverter breaker or wherever the power circuits are going from the array. That's very important. (In fact it's infinitely more important than an auxiliary electrode, because an auxiliary electrode isn't important at all.

)
Intersystem bonding devices are basically for non-power-supply conductors like the ones you mentioned.