Auxiliary Gutter Sizing

Status
Not open for further replies.

phil

Member
Location
Kansas
I understand the 20% fill of total cross-sectional area in regards to conductors. When calculating the total fill of conductors and splices is it based on 75% of the total cross-sectional area of the gutter or 75% of the 20% figure. The wording in the code is fairly clear, just want to make sure I'm reading it correctly. Thanks.
 
Re: Auxiliary Gutter Sizing

NEC 2002, 366.9(A) states "The conductors, including splices and taps, shall not fill the gutter to more than 75% of its area."
 