- Portland, OR
Replacing/relocating old fuse panel. Existing feeder to heat pump air handler/aux heater is #4 SE cable. Fused at 60 but draw/spec 48A. Using 60 degree column seems like 55 would be the max. Am I missing something, since this isn't the first time I've seen this. Have used 55amp breaker before but not readily available. Have used flex and #6 THHN with 60 breaker....should I be shopping for #3 SE or is there an exception I'm missing? Thanks.