auxillary gutter

Status
Not open for further replies.

jumathum

Member
I have 12"x12"x60" long auxillary gutter mounted above a section of gear. No wires are spliced inside, they are simply passing through. Am I required to identify my grounds and neutrals.
 
Grounded conductors would still need to be identified per 200.6 and grounding per 250.119 which, in sizes #6 and smaller requires continuous outer finish.
 
I agree with Gus, both the grounded and equipment grounding conductors would need to be identified in a wireway or auxillary gutter.

Chris
 