AV equipment shared neutral

Status
Not open for further replies.

Jason H

Member
Location
Colorado
Occupation
Journeyman
AV guys on this job are saying that the 12/3 circuit I provided for 2 projectors and 2 drop down screens aren't working because of the shared nuetral. I split the circuit so that 1 projector and 1 screen are on each leg. Total load for each set is 15amps and protected on a 20ocd. I don't see how a shared nuetral for this equipment would keep it from working properly. Has anyone had this issue before?
 
A/V guys are nuts when it comes to stuff like this. Ask them if it would be okay with the projectors on one circuit and the screens on the other.

I used a regular 50a 120/240 feeder and panel in my home theater, with some equipment on each leg. My system is dead quiet with no signal.

1642524380356.png 1642524453984.png 1642524526000.png
 
Very nice, whats the small yellow cord on the bottom right of your panel?
Why the recp outlets instead of plug strips?
 
I always used dedicated neutral on commercial A/V installations. On larger jobs i.e. university A/V classrooms I provided small isolation transformers 120/240 to have independent supply. Reason - harmonic distortion on shared neutral is cauisng problems. In theory on 120/240V THD should canel - but that only theory. Older guy told me too do this, never had a problem. Cost more to troubleshoot and rectify.
 
Very nice, whats the small yellow cord on the bottom right of your panel?
It feeds the panel from the 12v DC switched trigger output of my preamp-processor. The output is only capable of 15ma, so the yellow cable energizes a reed relay, which energizes a 10a cube relay, which in turn energizes a 4-pole 20a contactor, all inside the panel.

Four of the eight 15a circuits are switched through this contactor, and supply the two power amps, the two sub-woofer amps, and a few other components, like the plug-in LV power supplies, so the power switch on the preamp-processor can control the entire system.

I used the G.E. sub-panel because the breakers being offset from the center provided enough room for the relays and the contactor to fit inside the enclosure. I thought the cable channel was a good way to keep the power cords neat and away from the signal cables.

Why the recp outlets instead of plug strips?
I would still have needed several receptacles, some circuits only feed single components, like the power amps, the projector, etc., and I still would have needed a separate strip for each circuit supplying more than one component, so there would be no real advantage.

Each power amp has its own dedicated circuit, and the sub-woofer amps (built into the main speakers) share one. The main amp is rated at 300w x 2, the center/sides/rear-speakers amp is rated at 200w x 5, and the two sub-woofer amps are rated at 300w each.

That's a total of 2,200 watts of continuous power. The system will play at full, realistic concert levels without breaking a proverbial sweat. I have replaced the preamp-processor in the picture with a Fosgate FAP-T1+ unit that has a wide-screen monitor on the front.

1642532172845.png

1642532190833.png
 
On larger jobs i.e. university A/V classrooms I provided small isolation transformers 120/240 to have independent supply. Reason - harmonic distortion on shared neutral is cauisng problems.
How would your shared-neutral 120/240v transformer be different from the utility?
 
Apparently the circuit board on the projector lifts were bad. Replaced them yesterday and all is working fine. Thanks everyone.
 
As i said. "I always used dedicated neutral on commercial A/V installations." By dedicated I ment not shared.
 
As i said. "I always used dedicated neutral on commercial A/V installations." By dedicated I ment not shared.
But as Larry points out, the service is utilizing a shared neutral, so regardless of dedicated to the equipment a shared neutral is involved.