I am sizing a Delta secondary Hi-leg system for two 42 amp at 120 volt loads. I have reviewed the theory and I believe I will require a 75,Kva, Delta/Delta (due to customer requires 240/120 volt). I believe the math is; 75 Kva/3= 25 Kva. I am treating each 25 Kva winding or transformer as single phase therefore 25 Kva/240V=104.17A.
Am I correct that the available amps for 120 volt loads would be 52 amps from C1 to N and 52 amps from C2 to N since I am using half of the winding?
This is being provided for a single piece of equipment. The load requires two, single phase, 120 volt circuits of 42 amps each.
Thanks in advance.