Lance Campbell
New member
On a GE Spectra series distribution with a 400 amp main I have a rating on the cabinet of 10 kA rms sym. The 150 kva transformer is 50 feet away and has 2.5% imp. We ran 600 mcm copper to the main. When we do the fault calcs, we get 15,685 amps fault available line to line, and 15k line to neut. Is there any way I can be in compliance with this scenario, like short time current limiting fuses mounted on the transformer?