So, my company purchased a wax melting machine today and they want to integrate it into a machine that they want built "in-house". Problem is, the people that do the planning and buying have knee-jerk reactions to just buying whatever and then handing it off and telling someone to "make it work".
My first observation is the nameplate on the wax melter states that it has only 1,500A of Interrupt capacity. It is 230VAC single phase and needs 24Amps. Our transformers out on the floor give us 120/208 are 75KVA. So, without looking at the transformer impedance value I am just going to go ahead and assume that we are significantly higher than that (probably 5kA - 6kA).
What are my options at this point.
Do I have to install another transformer 7.5KVA based on the load requirements? 24A * 230V * 1.25(Safety Factor) = 6900W
Can I use Current Limiting Fuses? Or would this fall in line with needing "Engineering Supervision" (licensed PE)?
Does NEC 110.22 and 240.86 apply here?
Any advice would be appreciated. Thank you.
My first observation is the nameplate on the wax melter states that it has only 1,500A of Interrupt capacity. It is 230VAC single phase and needs 24Amps. Our transformers out on the floor give us 120/208 are 75KVA. So, without looking at the transformer impedance value I am just going to go ahead and assume that we are significantly higher than that (probably 5kA - 6kA).
What are my options at this point.
Do I have to install another transformer 7.5KVA based on the load requirements? 24A * 230V * 1.25(Safety Factor) = 6900W
Can I use Current Limiting Fuses? Or would this fall in line with needing "Engineering Supervision" (licensed PE)?
Does NEC 110.22 and 240.86 apply here?
Any advice would be appreciated. Thank you.