Is there a ‘quick and easy’ rule of thumb way to determine available fault current for a (power) Panelboard without doing complex calculations or using Etap?
Sent from my iPhone using Tapatalk
Yes. Follow the IEEE ANSI procedure! It was created at a time when calculators did not exist and computers took up a large office building.
Ok so first and least accurate method that I see used everywhere: infinite bus. Let’s assume all transformer losses are reactive (almost entirely true) and the utility bus is very stiff, much bigger than the transformer (sometimes true), and that there are no reactive loads, and all cables have no impedance. So really we just have one reactance. So we just calculate the transformer theoretical maximum short circuit current at the secondary terminals. KVA x 1000 / (1 or 1.732) / V / (%Z / 100) is short circuit current.
Ok but cabling makes a huge difference!! No problem. Look at the Cooper Bussman point by point method. It is a couple tables and formulas and napkin math. Slide rule optional!! It significantly reduces the value from infinite bus even with a little bus bar. And we can go through multiple cables and transformers in series (point by point).
The only thing point by point misses is DC transients. Those can be ignored with UL 1077 equipment (switchboards, switchgear) where everything has a 30 cycle rating unless you have some big synchronous machines with long time constants. So check for that. This is why the IEEE 1584 arc flash spread sheet uses point by point.
Ok, so still not good enough? You can use the full ANSI method. Get the reactance data for each cable. Get motor data. Throw out anything 25 HP or less (transient collapses in under 1 cycle). Add all motor HP from 30 to 150 HP and treat as one motor. Calculate transient reactance (current) from the ANSI tables. Calculate the resulting system using Ohms Law since everything is reactance only. I’m glossing over details but the procedure is really that simple. This is exactly what ETAP does. I’ve also got another simple one from a Soares book but it’s not in PDF or anything like that.
So you want resistance too? Same as above but use the full R+jX values. This takes longer and since resistance has very little impact on short circuit (1%) nobody does it.
This gets you within 10%. Need more accuracy? Then screw ETAP. You need one of the various EMTP programs and a lot of personal abuse! This does time series level analysis.
Remember NEC does not specify which method to use. This is where engineering judgement applies. For short circuit purposes our concern is whether or not SCCR is an issue. So if we do infinite bus or even point by point with just the feeder and we are well under SCCR, with no big synchronous machines or motors and X/R is reasonable, we are done. No need to go further. If it is way over we also have a result. But if it’s close, we need to use another method or just buy the bigger breaker.
With arc flash it’s a much worse problem. The math works in reverse. So if you overestimate short circuit current you will underestimate arc flash, by s lot. So arc flash calculations are best done with the most complicated model, full R+jX. ETAP, Easypower, SKM, etc. do this automatically. The short circuit report will be in ANSI but the arc flash uses the full model plus an adjustment on arcing current specified by the 1584 model,