sunny1
- Washington State
- electrician
Greetings,
I used a fault current calculator I found on here to determine what AIC rating for breakers would be adequate for a panelboard I plan to install. I'm not sure of the power factor, so I used the guidance on the spreadsheet that says to use 100% if unknown. I played with that number a little as well but in all cases, I believe I should be plenty good with regular 10K AIC rated breakers. I have reached out to the POCO regarding the utility fault current amps, but all the other values are good.
Is it more accurate to use the utility fault current vs. the transformer impedance (Z value) or would the result be the same? I must admit I don't often do this calc and was hoping someone could tell me if I'm on the right track. Thank you ahead of time!