AVAILABLE FAULT CURRENT CALCULATOR QUESTION

Status
Not open for further replies.

florida-sparkey

Senior Member
Location
Pinellas Park, Florida
Occupation
Master Electrician
Does anyone know if the great free calc by John S. for available fault current is applicable when the transformer (L-N) 120V fault is greater than the (L-L) 240V? I am using (Ver 2017.) If so, do I just insert the larger current as given by Power Co whether it be the L-N or the L-L? In this case, 50 KVA xformer has 13,900A L-L and 20,800A available L-N. Thank you in advance!
 

florida-sparkey

Senior Member
Location
Pinellas Park, Florida
Occupation
Master Electrician
So I did the math on a point to point using the exact Bussman formulas. I have answered my question. For his calc, you input the L-L fault as he does the 1.5 * L-L for the center tapped xfmr to get M. However, I think I found a fault in the program. I think the L-N in the version I have uses the wrong value for the final L-N fault. It should use 1.5 * I L-L * M. Or at least that is how is is preformed in the Bussman calc example given. Anyone know which is correct?
 

WA_Sparky

Electrical Engineer
Location
Vancouver, WA, Clark
Occupation
Electrical Engineer
I've always been instructed to use the worst case scenario out of the two numbers. If the SCCR values are within 5-10% of the OCP rated KAIC, ive just went to the next level of protection.
 