I'm working on a new build in a strip mall. The main transformer is 3 phase 120/208 and the main service comes in behind the first unit. The transformer feeds into an 800A MGP36800 breaker, then into a triple meter pack, and then into a 200A breaker for each unit. There are two of these setups behind the first unit that feed all 6 units. So, from the transformer to an 800A breaker, to the meter, to a 200A breaker then inside to the unit. There is a label near the 800A breaker that lists the available fault current at 37,000A. We are working on unit three, which is about a 100' run away. We are installing an NQ454L2 - Three-phase main lug QO bolt-on panel.
My journeyman is insisting that regular 10KA-AIC breakers will be sufficient, "because that's what the other company used in unit 4 (about 50' further down from the transformer)". Is this a high enough rating, will the available fault current really drop over 27,000A in 100'? Does the 800A or 200A breaker rated at over 65KA-AIC do anything to the downstream available fault current?
Another question, in the past I have always installed main breaker panels, not main lug. Does this setup violate the 6-handle rule if we load up the panel, or because there is a main disconnect after the meter outside, is this not an issue?
My journeyman is insisting that regular 10KA-AIC breakers will be sufficient, "because that's what the other company used in unit 4 (about 50' further down from the transformer)". Is this a high enough rating, will the available fault current really drop over 27,000A in 100'? Does the 800A or 200A breaker rated at over 65KA-AIC do anything to the downstream available fault current?
Another question, in the past I have always installed main breaker panels, not main lug. Does this setup violate the 6-handle rule if we load up the panel, or because there is a main disconnect after the meter outside, is this not an issue?