Greetings group I am looking for some Journeyman exam practice questions on available fault current if anyone has any they like to share. Thanks
I like to start the guys out with simple transformer impedance on a 75 KVA 480 to 120/208.
They always ask is this equipment good. I say let's find out. Then show them the time current curve of the breaker and see how it falls into the instantaneous range.
Then I remind them we need fault current to open OCPD. Bolted/line and ground fault.
Then relate that to good grounding/ bonding and ask, now how import is tightening up this connectors and couplings. Or sizing the wire type EGC correctly. Leading them into IT squared for conductor withstand ratings.
I love it when there face lights up when they get it.
A line to line and bolted fault is easy. The ground fault is when they really get it. If the wire is good and you have known resistance.
Now you bring in the ground fault and either a light bulb goes off or more training required. Starting with definition and low impedance.
The guys that get it tend to stick around and the rest go to the installer crews( shovels).