Re: Available fault current
We have 2 issues here:
1) Interrupt current rating of devices;
Interrupt current rating will give us a value that the device can safely interrupt without exploding. Bolted fault calculations are fine for this, as long as final transformer ratings are stable. Transformer impedance will limit the available fault current.
2) Arc fault current level;
This will give us a value for the HRC level and PPE required by our workers. This is the new kid on the block, a learning experience for all of us.
208V or 240V Panelboards connected to transformers less than 125 kVA can generally be ignored (IEEE 1584). These panelboards (IEEE) have a hard time sustaining an arc flash event, incident energies can be high due to long trip times, but the explosive nature of the event is subdued. With proper PPE, a 2 second exit time is sufficient for personnel to escape unharmed.
I cannot provide an answer to all the questions and scenarios on this thread. (NFPA has allocated funding so IEEE can further their research.) But I can pass on my results and management decisions based upon these results.
Number one on managements' list; NOBODY GETS HURT.
Number two on managements' list; HOW DO WE PREVENT ACCIDENTS.
Number three on managements' list; HOW DO WE IMPLEMENT NUMBERS ONE AND TWO COST EFFECTIVELY.
Back to the arc flash portion (interrupt rating has been settled).
The industrial facilities I have performed arc flash hazard studies on have either local generators or utility grid feeds. The facilities have internal, variable switchgear lineups. How does one handle all these variables and establish HRC levels and PPE requirements?
Well . . . Its' been tough!
Local utilities would not specify a range (min / max)of MVASC generation, but they would give me a typical MVASC, X/R at the substation (based on some weird base) and a statement that the substation is the current limiting device, no matter their online generation.
OK . . . So that is settled (assuming infinite trip time) just plug it into the modeling software . . . Hope for the best.
Switchgear lineup provides another layer of questions.
To make a long story short; Establish a STANDARD lineup with operations. All labeling is based upon this STANDARD. Next, for any equipment with trip times greater than 2 seconds (fight or flight instinct), re-run the arc flash calculations using 2 second trip times, label this equipment with a 2 second exit time notice. Then, train all supervisors, permit writers, operations and service technicians how to interpret the labeling.
With multiple generator lineups, run the arc flash calculations using the minimum and maximum STANDARD generators that could be online, adjust labeling for 2 second exit values as required.
Here in Alaska, medical resources are far removed from the work area.
Number one . . . NOBODY GETS HURT!
David Hippe P.E.