Jim10
Member
- Location
- Huntington, WV
This may be a stupid question, but here goes anyway...
We have a site where a 4 gang meter bank was installed with 200A mains for each, rated for 22kAic. The POCO has come back and said the available fault current at point of delivery is 22,025. The city has said they will allow the power install if an engineer signs off on it. Is that minor difference enough to require increasing the kAic rating of the bank and mains or is it small enough to be a safe install? I can also try to reach out to the POCO to get info to do a more complete fault current calculation if infinite bus was used if need be.
*DISCLAIMER this is the first of my involvement in this project haha*
Thanks
We have a site where a 4 gang meter bank was installed with 200A mains for each, rated for 22kAic. The POCO has come back and said the available fault current at point of delivery is 22,025. The city has said they will allow the power install if an engineer signs off on it. Is that minor difference enough to require increasing the kAic rating of the bank and mains or is it small enough to be a safe install? I can also try to reach out to the POCO to get info to do a more complete fault current calculation if infinite bus was used if need be.
*DISCLAIMER this is the first of my involvement in this project haha*
Thanks