coulter said:To insure the equipment you are installing has a high enough interrupt capacity to with stand and open a bolted fault (dead short).
Likely never be asked for a residential application. A 50kva xfm (3 - 4 houses), 1ph, 240V is about 200A FLC. At 5% Z (impedance), that gives 4000A fault current - well below most residential grade equipment.
carl
zappy said:protect the branch circuit brkr's?also how does a brkr trip if the fault happens on the line side of it?doesn't poco have fuses before it hits the service enterance conductors?i'm very ignorant about this stuff.i never seen this called by a inspector before.
zappy said:but wouldn't the main brkr with a 22,000 interup rating protect the branch circuit brkr's?
also how does a brkr trip if the fault happens on the line side of it?
doesn't poco have fuses before it hits the service enterance conductors?