The rating of the "gear" itself should be available from the gear manufacturer.
Determining the available fault current supplying the gear is an engineering function. If it is supplied by the utility, the utilty should be able to give you the current at their point of supply.
Given that number you can apply the factors that reduce the AIC (length on runs, wire sizes, etc; and current limitimng devices) and factors that can increase the AIC (such as motor contribution).
If the gear in question is fed by a transformer, if you can supply the transformer data (voltage, kva, impedance, etc) someone here can give you a "round number" , but exact AIC levels should be a product of an engineering study.,
(sorry richxtlc , I was posting on top of you.)