Available fault current

Status
Not open for further replies.

mshields

Senior Member
Location
Boston, MA
I thought I read either as a 2011 change or else where that the Available Fault current used for short circuit calculations now had to be based on infinite fault current on the primary of the service transformer? Is that true or do we still need to track the actual available fault current from the utility?
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Mike,
There is not any rule that I know of that says that. The new rule in 110.24 requires field marking of the available fault current on the service equipment at the time of installation.
 