180 FAULT CURRENT
180.1 The Company shall determine the available fault current at the delivery point. To do this, the
Company must know the Customer's service size, service voltage, detailed load information and the
location of the Company transformer and delivery point.
180.2 The Customer is responsible for the installation of protective equipment with an interrupting
rating sufficient for the maximum available fault current.
180.3 On initial services and reconnection after alterations to existing services, the Company will limit
the available fault current on single family detached homes (including mobile homes not in mobile home
parks) to 10,000 symmetrical amperes. This is provided the service size does not exceed 200 amperes.
For all other Customers, both on initial connection and reconnection of an existing service after
alterations, the Company will only notify the Customer of the available fault current.