awg necessary on disconnect and subpanel
hardworker
I am installing a 200 amp 1 phase disconnect within 2ft of an existing 400 amp main panel. The disconnect will feed a 200 amp subpanel about 60 ft. away.
Using 3/0 for the hots and #4 for ground. All copper.
Does code want something heavier between disconnect and main?
Thanks
Thanks
Just need the feeder breaker in the 400A to be large enough to protect the 3/0 wire. Which in your case would be a 200A breaker.
If this is a tap the EGC should be #3, its size based on the 400 amp OCPD ahead of the feeder that you're tapping.
Is there not a feeder breaker in the 400A panel?
It is not obvious why you are installing a fused disconnect switch within 2ft of another disconnecting means (the breaker in the panel).
I think he's saying he's pulling off the 400amp. Hitting a 200amp disco feeding a 200amp panel 60` away. If that's the case you fall within the 10' tap rule.
Sent from my SAMSUNG-SM-T337A using Tapatalk
I realize he may be doing a feed thru [tap]. Just looking for clarification.
There is not a feeder breaker in the 400 amp panel. I will have to tap it. It is an older installation.