Hello All,
Can anybody tell me the what is the configuration of PT used in the attachment? It has B phase grounded. I have read that the advantage with this is that the earth fault protection in the generator system can be set without any fear of it maloperating for a phase-to-ground fault in VT secondary circuits. But how come grounding the B- Phase avoids mal operation? The basic principle of PT is it should not be short circuited to
earth. Just for Imagination, if the neutral of the secondary is not grounded and the phase is grounded, Could we relate it to like
a single line to ground fault on ungrounded system. Then even this causes the operation of ground fault relay
Can anybody tell me the what is the configuration of PT used in the attachment? It has B phase grounded. I have read that the advantage with this is that the earth fault protection in the generator system can be set without any fear of it maloperating for a phase-to-ground fault in VT secondary circuits. But how come grounding the B- Phase avoids mal operation? The basic principle of PT is it should not be short circuited to
earth. Just for Imagination, if the neutral of the secondary is not grounded and the phase is grounded, Could we relate it to like
a single line to ground fault on ungrounded system. Then even this causes the operation of ground fault relay