After looking at the trip characteristic curves of B,C, and D type breakers, I think that B curve would be the best breaker to use for Heater applications. The time delay for these breakers is the minimum of the 3, and for a purely resistive load this is desirable.
The only problem I can see is when the purely resistive Heater load is switched on and off quickly by an SSR. Would such an application where the heater load is being controlled by a fast switching SSR actually need to be protected by a C-Curve breaker?
Does the Solid State Relay control even make a difference to the characteristic curve breaker I should choose? I know if the OCPD were a fuse instead of a breaker, I would not even consider any kind of time delay.
The only problem I can see is when the purely resistive Heater load is switched on and off quickly by an SSR. Would such an application where the heater load is being controlled by a fast switching SSR actually need to be protected by a C-Curve breaker?
Does the Solid State Relay control even make a difference to the characteristic curve breaker I should choose? I know if the OCPD were a fuse instead of a breaker, I would not even consider any kind of time delay.