I was getting 120 volt back feed from a refrigerator, no short to ground. Tested both 120v. circuit and refrig. But still was finding 120v to ground ???? No idea

(Edited to remove email address. If you wish to contact the poster by email, then first send a Private Message asking for the email address.)

[ April 07, 2004, 08:52 AM: Message edited by: charlie b ]
 

wyedelta

Member
Re: Back feed from Refrigerator

your message is not clear.but there are two possible cause for thar.
1.as mention the compressor might be grounded already/partially burned-checked resistance to ground(body as common test point and checked the CRS of the compressor- C as common R as running winding S as starting winding) if you get resistance motor is already grounded and must be replaced even though the motor is running good.
2.Something wrong with electrical wiring-checked the door switch/thermostat/fan motor(if any in the evaporator)those wiring might touch the body or in other words might be grounded.

for your voltage i assume that there is no neutral/ground otherwise when you checked the voltage to earth you will get 120V and 0 (only if the fridge is properly earthed)
 