Can i back feed a 60 amp breaker for a disconnect for a sub panel ?
 
Can i back feed a 60 amp breaker for a disconnect for a sub panel ?

see 408.36.D
2008 NEC
Yes, but it must be held in place by an additional fastener that requires other than a pull to release the device from the mounting means on the panel.
 
see 408.36.D
2008 NEC
Yes, but it must be held in place by an additional fastener that requires other than a pull to release the device from the mounting means on the panel.


Only if it is a plug-in circuit breaker, not required for a bolt-on, but plug-in type is more common.
 