maghazadeh
- Campbell CA
Hi everyone,
I am going to bend a 90, a kick, and second 90 on one 10 ft length piece of 2" EMT conduit using an old Green lee 855 smart bender with standard pendant. The same bends will be applied for 6 different runs of conduit. I will do the two 90 bends plus adding shrinkage for a 22-1/2 degree kick bend (between the two 90 bends), then at last I will bend the kick bend to avoid dog leg.
I have the instruction book that came with the bender, and there is plenty of information to bend 90, offsets, 3, 4 point saddle, and U-bends, but reading the special bending chart is confusing to me.
For a 90 stub up for a 2" EMT the chart says Minimum stub length = 18-3/8" and deduction (take up) for the mark #1 is 16-3/8".
The route that the conduits will take is;
50" straight up to the top of first 90 (out of cabinet) changing from vertical to horizontal plane.
Horizontal distance between the first 90 and the second 90 is 46" from outside-to-outside the conduit.
A 22-1/2 degree kick between the two 90 bends, changing direction in the same horizontal plane. ( shrinkage is 3/16" for every 1" of rise for a 22-1/2 degree bend) my directional change and/or rise is 11" so shrinkage that will be added to the length between the two 90 is
(11" x 3/16" = 2.0625"). So roughly 48" between the outside to outside of 90s.
As an example: back to back bends for a 3/4" EMT conduit, for the first bend measuring the same direction as bending deduct 6". Second bend, bending opposite direction to measuring add 3". these numbers will give a desired distance from outside to outside of the 3/4" conduit.
Question #1: Can I use the same principle as the example above for a 2" EMT?? Meaning for first 90 (50" - 16-3/8" = 33-5/8" bending mark #1).
Bending 2nd 90 opposite to measuring direction and using (half of deduct / take up amount 16-3/8" divided by 2 = 8-3/16") so,
distance between the 1st & 2nd marks outside to outside is ( 46" + 2.0625" shrinkage + 8-3/16" adder for 2nd mark = 56.25" or 56-1/4")
Question #2: does the calculation and steps above seems right to you?
Question #3: Is outside to outside measurement correct method for this size conduit?
Question # 4: Can you think of any easier way to achieve this challenge other than cutting the conduit between the bends and using couplings??
I'm pretty sure there are bunch of smart ones out there, so please help. Thank you in advance for any help I get.
Best,
Max
Best,
Max