Back to back receptacles

Status
Not open for further replies.

LJH

Member
In a wood structure hotel do fire pads work for back to back receptacles in the seperation walls for the rooms, versus the 24 inches seperation?
 

LJH

Member
back to back receptacles

back to back receptacles

Thanks Barbeer, and yes I am the AHJ, I ended up asking for the listing on the pads along with the elec. eng. rfi.
 

mdshunk

Senior Member
Location
Right here.
I keep finding language similar to this on the putty pad manufacturer's websites: "When moldable putty pad outlet box protective material is used on boxes on both sides of wall as directed, the horizontal separation between outlet on opposite sides of the wall may be less than 24 in. provided that the boxes are not installed back-to-back."

3M has a really nice PDF that lays it all out: http://multimedia.3m.com/mws/mediawebserver?66666UuZjcFSLXTt4XfEN8TcEVuQEcuZgVs6EVs6E666666--
 