I suppose this means EM-385-1-1 is also out?I can't use the 29 CFR 1926 because this isn't construction.
Well, that's an interesting question...If I'm not mistaken, that's an Army Publication?? I'll take a look!
What I find interesting is that the outer sheath is failing along the imprinted identification info. It would seem the imprinting process created a weakness/stress concentration in the sheath.
In the condition the cable is in, it is no longer as listed. The outer sheath has become useless and has been replaced by tape. Tape is not a Chapter 3 approved wiring means.
What I find interesting is that the outer sheath is failing along the imprinted identification info. It would seem the imprinting process created a weakness/stress concentration in the sheath.
electrical tape is actually listed as a means of repairing conductor insulation IIRC.
I am not sure I have a problem with repairing the conductors so much as whether conductors with appropriate insulation were used in the first place.
I guess that would be the 6 million dollar question Bob...is it the right cable. I will need to go back and find markings that aren't destroyed. I'd like to believe the contractor who put this stuff in, would have followed the NEC at the time of installation.
I guess that would be the 6 million dollar question Bob...is it the right cable. I will need to go back and find markings that aren't destroyed. I'd like to believe the contractor who put this stuff in, would have followed the NEC at the time of installation.
ARTICLE 555—MARINAS AND BOATYARDS
***
555.13 Wiring Methods and Installation.
***
(2) Portable Power Cables. Extra-hard usage portable
power cables rated not less than 167°F (75°C), 600 volts;
listed for both wet locations and sunlight resistance; and
having an outer jacket rated to be resistant to temperature
extremes, oil, gasoline, ozone, abrasion, acids, and chemicals
shall be permitted as follows:
(1) As permanent wiring on the underside of piers (floating
or fixed)
(2) Where flexibility is necessary as on piers composed of
floating sections
Since no cable is NEC approved to be installed where subject to physical damage, and the cable is obviously physically damaged, it was the wrong cable.
I agree with everything you have written here. I don't know what year the wiring was installed on the marina, so I cannot go back and say they did or did not do it properly in conduit. It obviously will have to be redone in conduit from now on. The sad thing is, that I am having to find justification to a government organization as to why electrical tape is not a viable option until New wiring can be installedHaving said that, it is possible this installation does not meet code anyway, given the use of cable in lieu of a proper raceway.
It does not appear to me that this is under the pier.
There are some additional requirements found in 555.13(B)(4)(5) if you try to invoke the flexibility option.
However, I am not an expert in marina wiring by any stretch of the imagination.
I agree with everything you have written here. I don't know what year the wiring was installed on the marina, so I cannot go back and say they did or did not do it properly in conduit. It obviously will have to be redone in conduit from now on. The sad thing is, that I am having to find justification to a government organization as to why electrical tape is not a viable option until New wiring can be installed
Sent from my SM-G920V using Tapatalk
While I completely agree...I don't know of anywhere in Chapter 3 that specifically says you cannot use electrical tape for repairs. I might just have to say that it doesn't say you "can" do it either.