You can kill utility workers.Originally posted by kunzio:
What hazards are there to backfeeding a dryer outlet with a portable generator?
702.6 Transfer Equipment.
Transfer equipment shall be suitable for the intended use and designed and installed so as to prevent the inadvertent interconnection of normal and alternate sources of supply in any operation of the transfer equipment. Transfer equipment and electric power production systems installed to permit operation in parallel with the normal source shall meet the requirements of Article 705.
Transfer equipment, located on the load side of branch circuit protection, shall be permitted to contain supplementary overcurrent protection having an interrupting rating sufficient for the available fault current that the generator can deliver. The supplementary overcurrent protection devices shall be part of a listed transfer equipment.
Transfer equipment shall be required for all standby systems subject to the provisions of this article and for which an electric-utility supply is either the normal or standby source.
406.6 Attachment Plugs.
(B)Attachment plugs shall be installed so that their prongs, blades, or pins are not energized unless inserted into an energized receptacle. No receptacle shall be installed so as to require an energized attachment plug as its source of supply.
Code violations aside, doesn't common sense factor in here as well?Originally posted by kunzio:
Can you point me in the right direction, as to where to find the code violations?
No I am pointing out that Article 702 is the Article of the code for optional standby systems and in order to connect those optional stand by systems 702.6 requires the transfer equipment to be designed and installed so as to prevent the inadvertent interconnection of normal and alternate sources of supply in any operation of the transfer equipment.Originally posted by kunzio:
"Iwire" Where are you relating the transer switch article to? Are you pointing out that there is a possiblity that once the utility power is regained, there could be multiple sources?
Jim, good post, concise and to the point.Originally posted by jimwalker:
Far too many utilty people have been killed over this.You could and should get charged with murder if you do this.Either do this in a safe way or use cords ran to generator
Yeah, it seems like that's the case. I'll let you know what side I choose in the morning.Originally posted by iwire:
Wake up on the wrong side of the bed today Pete?
I have long believed this but an article I read not all that long ago claimed this is an urban myth and that there are only a couple of cases on record where a backfed generator caused a utility worker's death and that none of them were from HO's doing this.Originally posted by jimwalker: