Is it within NEC code to backfeed a 125 amp main lug load center with a 60 amp circuit breaker? Doing this to lower the amperage at which the panel disconnects from the feeder, as the specifications call for.
408.36(D) Back-Fed Devices. Plug-in-type overcurrent protection
devices or plug-in type main lug assemblies that are
backfed and used to terminate field-installed ungrounded
supply conductors shall be secured in place by an additional
fastener that requires other than a pull to release the
device from the mounting means on the panel.
Is it within NEC code to backfeed a 125 amp main lug load center with a 60 amp circuit breaker? Doing this to lower the amperage at which the panel disconnects from the feeder, as the specifications call for.