versus establishing a neutral in the building
The neutral current from your 227 loads needs a path back to the source. (Generator)
Curious how you would do that?
The generator is almost definetly wye output, so bring the neutral out with you to the transfer equipment for the L-N loads.
If there are no L-N loads, then you can leave it at the first disconnect (be sure to bond it (N-G) if the transfer equipment is four pole).
There is no transfer switch, this is hooking up a portable generator to a building switch gear for temporary feed during an outage...
How are you ensuring that there is no power accidently fed back into the utility?
A transfer switch or some kind of interlock preventing both sources from being connected together needs to be used.
You have reviewed and are confident your proposed install will meet the requirements of 702.6 exception?
Actually I only have a 2002 code book with me currently... and in that 702.6 has no exceptions... what are the exceptions that may preclude a transfer switch being needed?
?Exception: Temporary connection of a portable generator without transfer equipment shall be permitted where conditions of maintenance and supervision ensure that only qualified persons service the installation and where the normal supply is physically isolated by a lockable disconnecting means or by disconnection of the normal supply conductors.?
Yes, now that I have found the exception, this would allow us to operate without a transfer switch, as we would be locking out the utility transformer main breaker and on stand by the entire time the building was running on generator...
The thing that may get you in trouble is how does your AHJ interpret "where conditions of maintenance and supervision ensure that only qualified persons service the installation"
We do have a good working relationship with our local inspectors and have already discussed that if we need to go on generator back up, we would have at least one electrician on site 24 - 7 while the building was being fed that way.
The other interesting scenario we need to address is the buildings fire pump.
The fire pump is fed on the LINE side of the main switchgear disconnect, so could NOT be fed temporarily without a transfer switch. So our inquiries are to have two generators one for the building gear and a seperate one for the fire pump. Then you get into the fact that since it is fed on the line side of the gear it is fed at a far greater ampacity than it draws. And it needs to be fed at full locked rotor current. That is quite substantial even though the conductors feeding it currently are not sized for that from the load side of the pressure rated switch feeding it. This is why we are truly relying on a engineer to decipher this to assure calculations and protocol is followed....
Anyone have any experience backing up a fire pump? I know I need to read up on the code sections but have not gotten through it all yet.
I haven't read that section in a while but if I recall correctly the conductors only need sized according to full load current (x 1.25) but the generator needs to b e capable of supplying locked rotor current indefinately.