richwaskowitz
Senior Member
- Location
- Shelby Twp. MI, near Detroit
Can anyone explain to me why a particular major residential backup generator manufacturer sets their automatic transfer switch to hang in until line voltage dips below 60%????? Isn't that awfully low? When I installed a 20 kW unit to backup our IT department at the office and I found this out, I added a programmable Siemens voltage detection relay to cut out at 90%. Am I the only one concerned about this? Do other manufacturers have similar settings?