Electriman

Senior Member
Location
TX
Greetings,
Does NEC require emergency shut down switch for back-up generator? Does it make a difference if it is a permanent installation or if it is a portable generator?

Thanks in advance
 
Yes if over 15 KW and permanent.


445.18 Disconnecting Means and Shutdown of Prime Mover.

(A) Disconnecting Means.
Generators other than cord-and-plug- connected portable shall have one or more disconnecting means. Each disconnecting means shall simultaneously open all associated ungrounded conductors. Each disconnecting means shall be lockable in the open position in accordance with 110.25.

(B) Shutdown of Prime Mover. Generators shall have provisions to shut down the prime mover. The means of shutdown shall comply with all of the following:

(1) Be equipped with provisions to disable all prime mover start control circuits to render the prime mover incapable of starting

(2) Initiate a shutdown mechanism that requires a mechanical reset

The provisions to shut down the prime mover shall be permitted to satisfy the requirements of 445.18(A) where it is capable of being locked in the open position in accordance with 110.25.

Generators with greater than 15 kW rating shall be provided with an additional requirement to shut down the prime mover. This additional shutdown means shall be located outside the equipment room or generator enclosure and shall also meet the requirements of 445.18(B)(1) and (B)(2).

2020 Code Language:

445.18 Disconnecting Means and Emergency Shutdown.

(A) Disconnecting Means.
Generators other than cord-and-plug-connected portable generators shall have one or more disconnecting means. Each disconnecting means shall simultaneously open all associated ungrounded conductors. Each disconnecting means shall be lockable open in accordance with 110.25.

(B) Emergency Shutdown of Prime Mover. Generators shall have provisions to shut down the prime mover. The means of shutdown shall comply with all of the following:

(1) Be equipped with provisions to disable all prime mover start control circuits to render the prime mover incapable of starting

(2) Initiate a shutdown mechanism that requires a mechanical reset

The provisions to shut down the prime mover shall be permitted to satisfy the requirements of 445.18(A) where it is capable of being locked in the open position in accordance with 110.25.

N (C) Remote Emergency Shutdown. Generators with greater than 15 kW rating shall be provided with a remote emergency stop switch to shut down the prime mover. The remote emergency stop switch shall be located outside the equipment room or generator enclosure and shall also meet the requirements of 445.18(B)(1) and (B)(2).

N (D) Emergency Shutdown in One- and Two-Family Dwelling Units. For other than cord-and-plug-connected portable generators, an emergency shutdown device shall be located outside the dwelling unit at a readily accessible location.
 
Generacs now ship with one outside and one inside.

The last Kohler I looked at had one on the inside of the enclosure if I remember correctly.
 