flywright52
Member
- Location
- Missouri
I work almost exclusively in residential, so I thought I would ask those of you with more experience this question. I am helping my church with a problem in a 3 phase branch to a pump house used for watering the soccer field. One leg of the 3 phase (480) is missing. I checked the voltage at the circuit breaker feeding the pump house and found 480 only between two legs (yellow-brown) and ~240 between the suspect leg (orange) and the other two (good) legs. I disconnected the wires from the breaker and checked for continuity on each pole. I got a short in two of the poles when the breaker was switched ON and open when OFF. The suspect leg indicated open in either the on or off position. I know this is a rookie question, but is there any other test I need to do before replacing the (expensive) breaker? I have attached a picture of the breaker.