Hey guys,

I came to do a service call and ran into something strange that I’m having trouble understanding. The customer said they had no power. I went to the panel and checked voltage. Like to like, nothing. L1 to neutral, 110. L2 to neutral, 110. I pull the meter and check the poco side and everything is normal. I rang everything out and everything checked out. Any thoughts?

Thanks in advance,
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Clarify, please.
At panel L1 to L2 = 0 ??
Line side of meter L1-L2 = 240 ??
 

Little Bill

Moderator
Staff member
Location
Tennessee NEC:2017
Occupation
Semi-Retired Electrician
Sounds like you have lost a leg. You get nothing line to line, but get a reading line to neutral. There is a 2-pole load on, could be the stove, dryer, water heater, etc, that is back feeding the other line. That is why you have a reading on both lines. You just need to find where you lost the leg.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Agree with Bill & note it is possible that it is a defective meter but I've found more often than not it's a poor connection somewhere.
 

TriednTrue

Member
Location
Texas
Occupation
Electrical Contractor
Sounds like you have lost a leg. You get nothing line to line, but get a reading line to neutral. There is a 2-pole load on, could be the stove, dryer, water heater, etc, that is back feeding the other line. That is why you have a reading on both lines. You just need to find where you
But the main breaker is off.
 