i need to know if someone else can confirm this test:
I find, on a service call, bad voltages when a 120v load is put on either phase: 200v phase A, 40v phase B... I know I have a bad neutral, so I brainstorm and since I only have a meter I perform this test:
I plug in a hairdryer at the washer outlet, (unplugging all electronic stuff), turn it on, which immediately changes the voltages at the panel (the hairdryer running at 40v, I didnt want to destroy it with phase A 200v) and then RUN outside, up a ladder, and test the overhead wires at the drip loop: bad voltages here too.
So, my question:
If my neutral was bad in the house (say in a crawlspace j-box or something) would the voltages be correct at the drop and then "change" at the fault?
PS as it turns out, I was right and it was a bad transformer at the pole, which PGE changed that day
I find, on a service call, bad voltages when a 120v load is put on either phase: 200v phase A, 40v phase B... I know I have a bad neutral, so I brainstorm and since I only have a meter I perform this test:
I plug in a hairdryer at the washer outlet, (unplugging all electronic stuff), turn it on, which immediately changes the voltages at the panel (the hairdryer running at 40v, I didnt want to destroy it with phase A 200v) and then RUN outside, up a ladder, and test the overhead wires at the drip loop: bad voltages here too.
So, my question:
If my neutral was bad in the house (say in a crawlspace j-box or something) would the voltages be correct at the drop and then "change" at the fault?
PS as it turns out, I was right and it was a bad transformer at the pole, which PGE changed that day