Two parter...
I'm putting together a proposal to re-feed a high mast light pole - according to the electrician on-site, there is a bad phase leg (with the actual problem lost underground somewhere upstream) and naturally, lamps are not operating.
The pole currently consists of 8-1000W hps lamps and is fed via a 40A-3P circuit breaker at 480V. The electrician has recorded current draws from 26 & 29A in the good phases.
First question is, why are those phases drawing so much? By my calculation, the total power feed (including some ballast lost) is about 9600W (or 11.6A per line). I realize that the lamps are connected single phase (480), but wouldn't that affect the phase currents and not the line currents?? These numbers seem too large - even with considerable voltage drop over the 1500' run.
The second question (which ties into the first) is: would the bad phase leg have a hand in this? And if so, that still doesn't explain why the original OCP was sized at 40A??
Thanks...
I'm putting together a proposal to re-feed a high mast light pole - according to the electrician on-site, there is a bad phase leg (with the actual problem lost underground somewhere upstream) and naturally, lamps are not operating.
The pole currently consists of 8-1000W hps lamps and is fed via a 40A-3P circuit breaker at 480V. The electrician has recorded current draws from 26 & 29A in the good phases.
First question is, why are those phases drawing so much? By my calculation, the total power feed (including some ballast lost) is about 9600W (or 11.6A per line). I realize that the lamps are connected single phase (480), but wouldn't that affect the phase currents and not the line currents?? These numbers seem too large - even with considerable voltage drop over the 1500' run.
The second question (which ties into the first) is: would the bad phase leg have a hand in this? And if so, that still doesn't explain why the original OCP was sized at 40A??
Thanks...