Ursahouse
Member
- Location
- Placer County, CA, USA
New construction. Background: Ufer grounding system for remote subpanel some 200 feet away from service entrance and meter main panel from transformer. Single phase power. Three wire from service entrance 200 amp main panel to 200 subpanel buried in 3-inch PVC conduit. I am using a plug-in type circuit tester which indicates a good ground at less than 10 ohms (not sure how the tester does that). Anyway, the plug-in circuit tester shows a green light indicating a properly wired circuit and ground to earth when testing the receptacles at the service entrance meter panel. There is a 8' or 10' ground rod buried next to and long with the timber service pole. This has all passed inspections. I have also installed the Ufer ground in the foundation of the building some 200 feet away. This passed inspection prior to foundation pour. Its been a few years and I am now completing the work at the subpanel. When I test a receptacle at the subpanel, I get a flash of green light and then it goes to dim red light mode. If I use this same plug-in circuit tester on receptacles located in another older house it gives a green light indicating the circuit and ground are good. I have the Earth ground (Green) and the Neutral conductor bonded together at the service entrance (inspected). I have the Earth ground (Green-Bare) and the Neutral wires separate at the subpanel. We are in a drought here. The ground is very dry now. The founding native ground upon which the Ufer ground foundation rests is fractured to sold high resistive rock. In some places there is clay in fractured zones. In places, there are dikes of granite stone which I had to use a backhoe mounted jackhammer to excavate the foundation upon which the Ufer ground is located. Now that I think about it, the concrete used has a REOMIX admixture that helps prevent water from passing through foundation. This is an earthen-bermed house and I wanted to keep moisture out of the slab. I think I have a very dry foundation and soil profile under the foundation (fractured to solid rock).
I want a proper grounding system for this house. I am not interested in doing only that which is required under NEC.
Questions:
1. Is it likely I have a "Bad Ufer Grounding System".
2. Given that I can not just drive rods into the rock substrate anywhere near the subpanel, is it advisable to go sum 50 feet away where the soil profile is similar to that which provides a good ground for the transformer and service entrance main panel?
3. Other options?
I understand the basic properties I am up against after reading at this site and other grounding issues where shallow or other poor soils conditions exists.
What say you?
Should I be concerned that the plug-in circuit tester
I want a proper grounding system for this house. I am not interested in doing only that which is required under NEC.
Questions:
1. Is it likely I have a "Bad Ufer Grounding System".
2. Given that I can not just drive rods into the rock substrate anywhere near the subpanel, is it advisable to go sum 50 feet away where the soil profile is similar to that which provides a good ground for the transformer and service entrance main panel?
3. Other options?
I understand the basic properties I am up against after reading at this site and other grounding issues where shallow or other poor soils conditions exists.
What say you?
Should I be concerned that the plug-in circuit tester