balance loads
sparky21
i want to know how to balance a panel board i have 1,3,6 = 1 neutral can i use 1,3,8 = 1 neutral and be ok with NEC
if 1,3 and 6 are all on the same neutral - it will have to be doubled in size, amperage wise. so if they are all 20A circuits - you need a neutral that can handle 40A, since circuits 1 and 6 are on the same leg.
~Matt
if 1,3 and 6 are all on the same neutral - it will have to be doubled in size, amperage wise. so if they are all 20A circuits - you need a neutral that can handle 40A, since circuits 1 and 3 are on the same leg.
~Matt
Huh? Circuit 1 is "A" phase, 3 is "B" phase, and (assuming a 3 phase panel) 6 is "C" phase.
To answer the OP's question, no you can not use 1,3,8 because 1 and 8 are on the same phase so what TOOL said above would apply here. You would need a neutral large enough to be able to handle double the current.
I assumed it was a single phase panel - Since he did not tell us that - thats all we can do, assume.
~Matt
Under the 2008 NEC the answer is no even if all three circuits were on different phases such as 1,3,12.
let;s assume that the panel is 3 phase and the load of the every single circuit is 20 amp breaker can you still get 1,3,8 with the same neutral or you have add another neutral or side it to number 10 wire?