Re: Balancing 3 phase loads
It is not a requirement that loads be balanced, but rather a good design practice. Balancing a load allows for maximum utilization & protection of equipment. If a 3 phase load becomes extremely unbalanced, one or more of the circuit protecting devices (fuses or Oil Circuit Recloser)will likely trip that phase of the circuit. In Distribution Design, the 3 phase electronic VWE is the way to go. The VWE senses large phase imbalances and is designed to trip all three phases if an extremity of this situation occurs, unless the settings are changed after sent from the manufacturer. In Plant Industrial Applications such as large 3 phase motors, if starter overloads do not trip and a fuse is blown on the circuit that is unbalanced, a "Single Phase" situation will occur. If this happens, the windings of the motor will likely be damaged and the motor will have to be removed from service until properly rewound or disposed of if completely non-repairable.