jjs
Member
- Location
- Puryear, TN, USA
There are no receptacles on this balcony. I do not believe it is LIKELY TO BECOME ENERGIZED.
The inspector said lightning was not what he was referring to. What was mentioned was Christmas lights and TVs, connected to a receptacle located inside the house.
"250.4(A)(4) Bonding of electrically conductive materials and other equipment. Normally non-current-carrying electrically conductive materials that are likely to become energized shall be connected together and to the electrical supply source in a manner that establishes an effective ground-fault current path."
I have never had this request before in all the condo/apartment type buildings I have ever designed.
Does metal furniture inside the apartment have to be bonded then as well? How would you control that?
Where does it end?
The inspector said lightning was not what he was referring to. What was mentioned was Christmas lights and TVs, connected to a receptacle located inside the house.
"250.4(A)(4) Bonding of electrically conductive materials and other equipment. Normally non-current-carrying electrically conductive materials that are likely to become energized shall be connected together and to the electrical supply source in a manner that establishes an effective ground-fault current path."
I have never had this request before in all the condo/apartment type buildings I have ever designed.
Does metal furniture inside the apartment have to be bonded then as well? How would you control that?
Where does it end?