HW Saturation:
High output current condition detected (greater than 400% of rated output current). On B2 size controls, a desat error can indicate any of the following: low line impedance, brake transistor failure or internal output transistor overtemperature.
Started a seasonal operation today, attempted anyway, after a winters worth of moving equipment. An auger with a Baldor drive plugged & shut down. After clearing, resetting & getting it started again it will no longer operate the motor either with or without a load above 28 Hz. Same setup has worked for years @ 40 hz and worked part of yesterday and a good share of the morning. One of the faults is listed above.
We are about 300' from the service, #12 to drive, with line & load reactors, Voltage is 500+ which is typical for this plant. 5hp. I am guessing drive failure but sure would take some hints. A drive will be difficult to get tomorrow but can & will be done if needed.
Started a seasonal operation today, attempted anyway, after a winters worth of moving equipment. An auger with a Baldor drive plugged & shut down. After clearing, resetting & getting it started again it will no longer operate the motor either with or without a load above 28 Hz. Same setup has worked for years @ 40 hz and worked part of yesterday and a good share of the morning. One of the faults is listed above.