ctaylo360860
Senior Member
- Location
- colorado
- Occupation
- ME
Have a couple questions about a class 1 division 2 motor and pump.
So they changed existing motor and pump seen in picture #1 to the motor and pump in pic#2
The existing motor had a ground lead that ran from j box into the sealed motor. The new one did not. I did not notice this until I got the conduits put back together and got ready to terminate….
As I was also looking for the wiring diagram the pump guys handed me the outlet box that they removed from the motor.
Question 1 - will the rigid conduit be a sufficient means of bonding ? or am I going to need to break everything back apart install the outlet box on the motor and get an egc to the terminal inside the outlet box 3” away from the jbox?
Question 2 - when the pump guy removed the the outlet box did he void any type of warranty on the motor?
Motor is 240 single phase 2 hp. When I spoke to Baldor the rep said the motor and outlet box are listed separately… he suggested the box go back on if it were to be sent in for warranty, but wouldn’t give direct answer if it being taken off would void it…
I have looked over 501.30 a and b and I don’t believe I meet the exceptions…
I also looked of 430.12(e) but i don’t beleice that the exception would apply here as well…
I am Hoping that this is a compliant install with out the outlet box going back on and running a egc 6” from j box to motor outlet box!?
I think installing the outlet box on the motor and running the egc would be a much safer install, and will pry end up being the method I chose to fix this but I wanted to learn something and find out if it was or wasn’t compliant..
Thanks in an advance I really appreciate all of you and your help!
So they changed existing motor and pump seen in picture #1 to the motor and pump in pic#2
The existing motor had a ground lead that ran from j box into the sealed motor. The new one did not. I did not notice this until I got the conduits put back together and got ready to terminate….
As I was also looking for the wiring diagram the pump guys handed me the outlet box that they removed from the motor.
Question 1 - will the rigid conduit be a sufficient means of bonding ? or am I going to need to break everything back apart install the outlet box on the motor and get an egc to the terminal inside the outlet box 3” away from the jbox?
Question 2 - when the pump guy removed the the outlet box did he void any type of warranty on the motor?
Motor is 240 single phase 2 hp. When I spoke to Baldor the rep said the motor and outlet box are listed separately… he suggested the box go back on if it were to be sent in for warranty, but wouldn’t give direct answer if it being taken off would void it…
I have looked over 501.30 a and b and I don’t believe I meet the exceptions…
I also looked of 430.12(e) but i don’t beleice that the exception would apply here as well…
I am Hoping that this is a compliant install with out the outlet box going back on and running a egc 6” from j box to motor outlet box!?
I think installing the outlet box on the motor and running the egc would be a much safer install, and will pry end up being the method I chose to fix this but I wanted to learn something and find out if it was or wasn’t compliant..
Thanks in an advance I really appreciate all of you and your help!