Contractor asked my opinion and I'll ask yours.
Ball field lighting:
400 amp fusible disconnect feeds (2) 200 amp MB single-phase 240 v panels with 30 amp branch circuits to various 1000w Metal-Halide Fixtures.
Both 200 amp breakers are tripping after 15 or 20 minutes of operation (no 30s tripped).
Measured load when the lights are first energized is approx 125 amps per phase (equal), Over time to load will increase to 147 amps per phase.
Most likely reason for the main breakers to trip is__________________ ?