ballast fusing / disconnecting

Status
Not open for further replies.

dinkelja

Member
I thought I would query some people about their opinion on NEC 410.72(G), as we are about to write it into our spec permanetly, forever, hardcore, and without much input from me. Right now, I'm working on a light industrial / manufacturing facility lighting. I hope they have the ability to meet exception 4, at least.
I have a layout of about 350 industrial strips flourescents, about 5 ckts, in a wharehose outside the production area, 25 isles or something like that. Anyways, I was told to fuse and sta-kon each ballast Has anyone ever fused each ballast, not being a field elecrtrician, I don't know what that device would look like (precicesly I mean). I don't believe the ballasts are internally fused or even have a thermal OL :( If the ballast failed wouldn't it more than likely quit, instead of tripping, and continuing to trip a breaker? The engineer was worried about it taking out the whole circuit and CB not being able to reset. There will be about 70 fixtures on a ckt. I thought I could provide an egress fixture with internal battery backup in each isleway incase a ckt failed anyways. To cover the argument that we won't leave them in the dark, (the area is not occupied continuously), until they can get the ballast replaced.
What bothers me isn't so much the estimated doubling the cost of connecting the lights, and marginal labor increase, but the principal of over doing installations. Safety wasn't given as a reason supprisngly; while I see increasing equipment / personell protection vs increasing equipment / connection failure could be debated. Opinions please, thx.
 
How much do the ballasts cost each? If they are pretty cheap I would pop one open and check if there is a fuse, hopefully it is not potted (filled with black tar). I work at a lighting controls company where we design ballasts and we have fuses in all of our ballast designs.
 
Most modern ballasts are thermally protected, so seperate fusing should not be needed. A defective ballast will take itself out without tripping the circuit breaker or blowing the fuse.
 
dinkelja said:
I thought I would query some people about their opinion on NEC 410.72(G)

(snip)

I was told to fuse and sta-kon each ballast Has anyone ever fused each ballast...
You understand that 410.72(G) does not require supplemental overcurrent protection, just a disconnecting means, right?

Given the "effective 1/1/08" language you need do nothing now, and I believe it is generally assumed that the manufacturer is going to take care of this from the factory, IMO.

I think all fluorescents have the equivalent to thermal protection already, but I could be mistaken there. I never thought much of it, we have never been required to add anything in the field.
 
Any electronic ballast I have popped open had a fuse on the PC board...soldered in place of course but a fuse none the less.:smile:
 
I was wondering how you would go about fusing those lights, do you mean individual ballasts, or say at the beginning of an isle for the entire connected strip?
 