Hi, I was changing a ballast when I noticed this ballast. If you look at the diagram on the ballast, it shows a switched gray connected to the neutral. I was just wondering what is this all about? Thank you for your help.
 

Attachments

  • IMG_0873.jpeg
    IMG_0873.jpeg
    367.2 KB · Views: 41

Fred B

Senior Member
Location
Upstate, NY
Occupation
Electrician
A disconnecting means shall be provided that also disconnects the grounded conductor.
410.130(G)(2) Disconnecting means.
(2) Multiwire Branch Circuits.
When connected to multiwire branch circuits, the disconnecting means shall simultaneously break all the supply conductors to the ballast, including the grounded conductor.
 

zappy

Senior Member
Location
CA.
A disconnecting means shall be provided that also disconnects the grounded conductor.
410.130(G)(2) Disconnecting means.
(2) Multiwire Branch Circuits.
When connected to multiwire branch circuits, the disconnecting means shall simultaneously break all the supply conductors to the ballast, including the grounded conductor.
So what is the grey wire for? There is a white wire already.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
It seems strange that you can accomplish the number of lamps selection by connecting the gray wire to either the white or black supply conductor.
 

Flicker Index

Senior Member
Location
Pac NW
Occupation
Lights
It seems strange that you can accomplish the number of lamps selection by connecting the gray wire to either the white or black supply conductor.
I suspect it's intentional to allow for flexibility in replacement or OEM supply applications into an existing system. Since it's not standardized, one brand might switch the control wire to black to activate the second bank of lamps while another brand do so by switching to white. When used for service replacement, this one can go into either system configuration.
 