e2me
Member
- Location
- South Dakota
OK I came across a Bank Calculation on my test and now Im not sure if I got it right or not I will give you the exact wording and then my answer.After looking in Mike Holt exam prep book and Tom Henerys same I get 2 different answers and Not sure that mike is right so you decide.
What is the service calculated load for a 30,000 sq ft bank
my answer is 30,000x3.5x1.25= lights 131,250va
outlets as per 220.14k no # of so 1va X30,000 30,000va
total of 161,250va
or 16.1kva or 672Amps
Tom henery same answer but mike holts answer by 2005 exam prepbook unit 11 question 25 is 151,250va or 630 amps
seems Mike thinks you can apply the derates of 220.44 to receptical loads that are not figured by the 180 va required in 220.14I
So before I take my City Test I would like to know which is right .By the way I passed my State Exam with a 89% thanks to all who post here and answer my questions ,as well as others .It truely does help. Not only do I get answeres but other ideas from around the country as I relize my juristiction is not alwasy enforcing it the same as yours but good to see reasons they think different.:-?
What is the service calculated load for a 30,000 sq ft bank
my answer is 30,000x3.5x1.25= lights 131,250va
outlets as per 220.14k no # of so 1va X30,000 30,000va
total of 161,250va
or 16.1kva or 672Amps
Tom henery same answer but mike holts answer by 2005 exam prepbook unit 11 question 25 is 151,250va or 630 amps
seems Mike thinks you can apply the derates of 220.44 to receptical loads that are not figured by the 180 va required in 220.14I
So before I take my City Test I would like to know which is right .By the way I passed my State Exam with a 89% thanks to all who post here and answer my questions ,as well as others .It truely does help. Not only do I get answeres but other ideas from around the country as I relize my juristiction is not alwasy enforcing it the same as yours but good to see reasons they think different.:-?